What size UPS should i get for a two cabinet definity system. I will also be plugging in the Intuty VM and our CDR PC.
thanks in advance.
verde
 

I would check the power consumption of each device. For example: 700VA for each carriers and 300VA for each PC, together they consumpt 2000VA. Then I would buy a minimum 2KVA UPS.

Another factor that you need to consider is the duration of the UPS power, this has to do with batteries capacity. For a small UPS, you have no choice for capacity because the box limits what physical batteries you can install.

You may want to post the same question at the General UPS Discussion forum.

KCBell
 
Correction on my last post...

If all devices consumpt 2KVA then I would buy a 4KVA UPS....

Sorry....
 