Let me start off by saying that I am a fire alarm technician by trade. I don't know much about phone systems.
I service a campus-like site with many small buildings. There are 40+ fire alarm panels at this site which all communicate with an alarm receiver via analog copper phone lines through a Meridian PBX. Recently we have been replacing some of the older fire alarm systems with newer panels. The newer panels utilize Ademco Contact ID as the preferred reporting protocol. For those not familiar with Contact ID, a brief overview can be found here: [URL unfurl="true"]http://li0r.wordpress.com/contact-id-protocol/[/url]
Contact ID signals are transmitted in groups of 16 DTMF digits; each digit has a duration of 50 ms followed by 50 ms of silence. The standard relies on specific timing of the digit and receiver acknowledgement tones.
What is happening on this site is that the PBX seems to be "slowing down" the DTMF tones to the alarm receiver. The signals sound okay with proper 50 ms timing from the fire alarm panels inbound to the PBX; however outbound from the PBX to the receiver the DTMF tones are being lengthened to about 200 ms. The receiver never gets a chance to acknowledge the signals before the fire alarm panel tries to resend them. Unfortunately the people who manage the PBX have no clue how to fix this, so here I am. I would appreciate any help!
I service a campus-like site with many small buildings. There are 40+ fire alarm panels at this site which all communicate with an alarm receiver via analog copper phone lines through a Meridian PBX. Recently we have been replacing some of the older fire alarm systems with newer panels. The newer panels utilize Ademco Contact ID as the preferred reporting protocol. For those not familiar with Contact ID, a brief overview can be found here: [URL unfurl="true"]http://li0r.wordpress.com/contact-id-protocol/[/url]
Contact ID signals are transmitted in groups of 16 DTMF digits; each digit has a duration of 50 ms followed by 50 ms of silence. The standard relies on specific timing of the digit and receiver acknowledgement tones.
What is happening on this site is that the PBX seems to be "slowing down" the DTMF tones to the alarm receiver. The signals sound okay with proper 50 ms timing from the fire alarm panels inbound to the PBX; however outbound from the PBX to the receiver the DTMF tones are being lengthened to about 200 ms. The receiver never gets a chance to acknowledge the signals before the fire alarm panel tries to resend them. Unfortunately the people who manage the PBX have no clue how to fix this, so here I am. I would appreciate any help!