Cabinet Alarm

Cabinet Alarm

Cabinet Alarm

(OP)
After an inadvertent power down (contractor turned power off instead of bypass on generator), we still have a cabinet alarm on an Option 61 AC system (it is a CS1000M, but still looks like the good old 61, if you need perspective on the platform).

All the AC power packs and ring gens look normal to me -- not to mention the system appears to be working fine since the incident more than 36 hours ago.  

- any ideas what else we need to check?
- is it possible to get a system message that indicates the source of the alarm
- is it possible to manually clear the alarm (and if the issue is already cleared, the system will leave the LED off, but if the issue still exists, it will light again) -- this is possible on an NEC 2400 IPX and is quite handy?

Please let me know.  Thanks.

RE: Cabinet Alarm

ld 37
stat xsm

ld 137
cmin all
cmaj all

john poole
bellsouth business
columbia,sc

RE: Cabinet Alarm

As John insinuated it could be a either a power problem or a faulty system monitor board.  I would also go to ld 22 and print out your history file look for anything strange in the Sysload/INI sequence.  Also check the midnight routines.

RE: Cabinet Alarm

also make sure your fans are working below

It's only dialtone-VZ

RE: Cabinet Alarm

Check the UPS connection to the power monitor card.  Some are set to monitor UPS health with a contact closure.

RE: Cabinet Alarm

(OP)
Unfortunately, the stat of the xsm in LD 37 yielded nothing, but I did see some XSM messages in the history I was able to capture after I was informed of the power outage (I extracted only a couple of these lines as they were all the same).  Not sure if this provides any additional hint as to the problem.


>ld 37

IOD000  
.stat xsm


.stat


TTY  0 : ENBL   DES: systemmonitor
TTY  1 : ENBL   DES: RSMCDIALUP
TTY  2 : ENBL   DES: RSMCONLINE
TTY  3 : ENBL   DES: OnSiteTech
TTY  4 : ENBL
TTY  5 : ENBL
TTY  6 : ENBL NRDY
TTY  14 : DSBL   DES: PTY
TTY  15 : ENBL   DES: PTY
.
OVL000

% PWR000 XSMC 00 0 0
% PWR000 XSMC 00 0 0
% PWR000 XSMC 00 0 0


RE: Cabinet Alarm

XSMC 00 0 0 is a good thing.
But not seeing anything for other cabinets.
It should look something like this:
PWR000 XSMC 00 0 0

PWR000 XSMC 01 0 0

PWR000 XSMC 02 0 0

PWR000 XSMC 03 0 0

PWR000 XSMC 04 0 0

PWR002 PWSP 05 2 1

PWR000 XSMC 06 0 0

PWR000 XSMC 07 0 0

If you notice it shows here a pwr002 pwsp 05 2 1
That is because on pedestal 5 I have module 2 powered down.

You should be getting a report for each pedestal.  Check to make sure your line cords string from power monitor to power monitor.  If they are there you may have a bad system monitor in pedestal 0.

RE: Cabinet Alarm

(OP)
Actually we only have one pedestal [one pedestal stacked 4 high --- 2 CPU/Net and 2 IPE).

RE: Cabinet Alarm

Then I would say that the system monitor board is bad.  I didn't see anything in your short printout to indicate a problem.  To replace the system monitor board make sure you first disable the system monitor port in ld 37.
If you don't know what the port number is simply go to ld 37 and do a STAT on TTY.  It's usually TTY 0 but not always.
Sequence of events should be:

got to ld 37
REQ DIS TTY X
remove cables from system monitor.
remove system monitor
Check dipswitch setting on new system monitor
install new system monitor
replace cables to system monitor
REQ ENL TTY X
REQ STAT XSM

RE: Cabinet Alarm

(OP)
If it was a bad system monitor board, would (could) it still be showing ENBL?

TTY  0 : ENBL   DES: systemmonitor

RE: Cabinet Alarm

Yes it would / could

RE: Cabinet Alarm

If you want you could try disabling it, reseating it and re-enabling it.  I've seen that work before, but when that happens it's usually just a matter of time before it goes altogether.  Your Fans are running aren't they?  I didn't see a reply from you on that question.

RE: Cabinet Alarm

(OP)
I think so, but actually I am at a remote site and am trying to see if I can direct a local person to check a couple of things.  

We have a maintenance contract so when it appeared that we might have to do some physical troubleshooting, we called the vendor to come in and address.  

Actually, I am not even sure I know which card is the sysmon card (from where you indicated "disabling it, reseating it and re-enabling it").  Is it a small card on the back of the pedestal?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Tek-Tips Forums free from inappropriate posts.
The Tek-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Tek-Tips forums is a member-only feature.

Click Here to join Tek-Tips and talk with other members! Already a Member? Login

Close Box

Join Tek-Tips® Today!

Join your peers on the Internet's largest technical computer professional community.
It's easy to join and it's free.

Here's Why Members Love Tek-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close