Well, whatever solution you choose, keep one thing in mind, a server with 2 power supplies normally does lad balancing between the two supplies.
Meaning, if you place one on a UPS and for example the other one not, and the one NOT connected to the UPS fails, the one connected to the UPS will draw a double capacity from the UPS. So in this case you may never exceed 50% of load on the UPS, or the UPS can fail if the power goes down and the power supplies try to drain all they need from the UPS, doulbing the load on the UPS.