We have had a few PSU issues with some Catalyst 3550-24 Inline Power switches. It seems several of the internal Switch Mode PSU's have gone pop. Not a big issue really since this is likely to be the first thing that goes bang anyway? The problem is we have up to 3 of these switches connected to a APC UPS 3000, when the PSU goes it takes the 20-Amp C-Type input breaker of the APC UPS with it (this leaves the UPS running on batteries for a few hours until they have discharged as the mains input has 'tripped'). We have checked and there is a 10-Amp fuse in the 3550 switch and I would have thought this would blow before the 10-Amp input breaker to the UPS?
This is what appears to be happening and APC are questioning the Catalyst 3550. I would have thought the UPS(UPS's as there are loads of them....) was at fault? My electrical theory is non existent so any pointers as to what this is likely to be would be helpful. APC say the outputs on the UPS are not fused.
Thanks
Andy
This is what appears to be happening and APC are questioning the Catalyst 3550. I would have thought the UPS(UPS's as there are loads of them....) was at fault? My electrical theory is non existent so any pointers as to what this is likely to be would be helpful. APC say the outputs on the UPS are not fused.